Hot water tank heats up and then pilot out lght

Started by skloon, August 20, 2019, 05:27 PM

Previous topic - Next topic

0 Members and 1 Guest are viewing this topic.

skloon

Attwood GH6-6E Last trip out it wouldn't light- I bypassed the thermostats and it worked fine- I cleaned the contacts for the thermostats and now it starts fine and heats up then it shuts off and I get the 'pilot out' light on the control panel- if I switch off and on again it works fine againe until it heats up, I would suspect the thermostats but I did just replace both less than a year ago


BrandonMc

Mine will work for a while, and then for some reason randomly just kicks off and that red light at the control panel indicates a fault - or at least it does now. It would be good to know what others have done because I am in the same position.

Rickf1985

Have you cleaned the area around the pilot from any rust or debris and also have you set the pilot flame setting height and so that it is running on the flame sensor. Any of these will cause it to go out.

BrandonMc

Quote from: Rickf1985 on August 20, 2019, 07:10 PM
Have you cleaned the area around the pilot from any rust or debris and also have you set the pilot flame setting height and so that it is running on the flame sensor. Any of these will cause it to go out.


didn't know I could adjust that aspect. interesting... 

Rickf1985

You will see a small screw on the control that is usually marked with a "P".

skloon

Nope will look at that- although it does heat up it's only after it heats up it shuts off


DaveVA78Chieftain

An Atwood GH6-6E is a DSI model and does not have a pilot light.  The light represents Water Heater Lockout

WATER HEATER LOCK OUT - GAS AND SPARK PRESENT

  • Gas pressure incorrect: Set inlet pressure at a minimum 11? W.C. with two or more gas appliances running
  • Low voltage: Correct power supply - 10.5 VDC minimum
  • Poor electrical ground: Secure electrical ground
  • Electrodes out of flame pattern: Re-adjust electrodes
  • Electrodes sparking to screw fastening burner to flue tube Adjust electrodes away from screw
  • Dirty electrodes: Clean electrodes
  • Partial obstruction in main burner: Clean main burner
  • Partially obstructed main burner orifice: Clean main burner orifice or replace
  • Improper air adjustment: Adjust main burner air shutter approximately 1/4 open
  • Flame spreader on main burner out of adjustment: Adjust flame spreader so that it is square to the end burner tube out of alignment of the main burner
  • Manifold not aligned with main burner: Re-align solenoid valve with main burner
  • Partially opening solenoid valve: Replace solenoid valve
  • Defective circuit board: Replace circuit board
[move][/move]


Rickf1985

I also thought it was electronic but when I looked up the manual it shows a regular pilot light.
https://www.manualslib.com/products/Atwood-Gh6-6e-9990191.html

DaveVA78Chieftain

Rick, that manual covers Pilot, DSI, and the new XT model units.  The "E" at the end of GH6-6E designates DSI.  If it was a pilot model it would just be GH6-6.
THere is a Atwood Model Brochure along with a Troubleshooting guide in the Members area under Water Heaters.
[move][/move]


BrandonMc


skloon

My Atwood gh6-6e hot water heater starts up fine when I hit the switch, the water heats up then when it reaches temperature the burner turns off, I hear the ignitor spark for about 2 seconds then it stops and I get the pilot out light on the control panel- If I turn the switch off and on again it lights. I have cleaned out the burner tube and checked the air gap, cleaned the orifice and the thermostats are 2 years old